Gents,
I would like to know if it is possible to deactivate only Phase A. My house is connected to the electrical grid using two phases.
Shelly is showing wrong power and current.
Thanks all.
Carlos Filho
VPN/Proxy erkannt
Es scheint, dass Sie einen VPN- oder Proxy-Dienst verwenden. Bitte beachten Sie, dass die Nutzung eines solchen Dienstes die Funktionalität dieser Webseite einschränken kann.
Gents,
I would like to know if it is possible to deactivate only Phase A. My house is connected to the electrical grid using two phases.
Shelly is showing wrong power and current.
Thanks all.
Carlos Filho
Change the device profile to „Monophase“. (Assume you have a Shell pro 3EM - title and category are different!)
Is it not possible to simple NOT connect current sensor A and voltage connection to phase A? If not supplied Shelly PRO 3EM should "measure" 0V and 0A = 0W on phase A (with a good hardware designe).
As I remember the Shelly PRO 3EM itself is supplied with phase C.
It is possible to operate the Shelly in Triphase mode with channels A and C or B and C. Channel C ist obligatory because the supply voltage for the device is fed via terminal C.