Shell 3EM - single phase - No Neutral
  • Hello everyone
    I am currently looking into the Shelly options to monitor my energy consumption.
    I was wondering whether or not the Shelly 3EM is an option in my situation, which (I think) is comparable to the situation mentioned in this topic but I did not want to hijack that topic.
    Incoming:
    My board mentions 2x230v, this has no neutral (I always thought the blue cable was supposed to be neutral)
    I wanted to have a power measurement of the consumption while taking into account the production of my solar array.
    I know the 3EM is focuses on multiple phases but this diagram seems to be the situation I am in.
    Is this something that the Shelly 3EM (or EM) supports?
    Thanks in advance!
    Some visuals:
    cable connection after the (analog) consumption meter:
    Main breaker:
    Incoming my electrical board, main differential:
    Bridge at my main differential:
    Einmal editiert, zuletzt von JanVG (21. September 2022 um 13:11)
  • Obviously, the blue wire can be considered as neutral wire, also the grey wire after the RCD (bridged at the input of RCD). Thus, this diagram would fit:
    448-ar768-einphasige-wandlermessung-png
    To measure the total consumption, only one current clamp is necessary. But you may use the remaining clamps to determine the consumption of particular consumers.
    And, by the way: Welcome to the forum!
  • Hello thgoebel
    Thanks you for your welcome and very quick response.
    Is my assumption correct that for each clamp (IA,IB,IC) I need one live wire into a V-port?
    So if I only use 1 clamp on IA I need to put one cable in VA?
    If i were to put it behind an existing breaker in my board, would this be a correct wiring (without a clamp for the solar array)
    The live wire from the breaker to VA
    The neutral wire from the breaker to N
    A clamp on the black wire (not sure about this?) to IA
    To add a measurement for solar:
    wago on live wire and add a cable to VB?
    Clamp from IB to live wire of the solar array, direction inverter -> breaker for the solar array?
    Thanks in advance and sorry for the many questions :D
  • Is my assumption correct that for each clamp (IA,IB,IC) I need one live wire into a V-port?
    Yes, indeed!
    Agree with your thoughts to install the clamps and voltage pick up. But you should consider to use a Shelly EM if you want to measure not more than two power consumptions at one phase. It would be cheaper…
  • Thank you for your input!
    I think I know enough to get some measurements going and feed the data into my home assistant.
    On a sidenote, I have been looking into the EM instead of the 3EM, but the availability seems to be an issue. I will find a use for the third clamp f.e. measuring a circuit where some older appliances are present might be insightful.
    Thanks again!