Addendum:
If it’s desired and allowed, the whole VASCO unit could be switched on/off by a third Shelly 1:
(Switching inputs SW were omitted intentionally)
But you should check in prior if the unit is built for frequent power cycles!
Addendum:
If it’s desired and allowed, the whole VASCO unit could be switched on/off by a third Shelly 1:
(Switching inputs SW were omitted intentionally)
But you should check in prior if the unit is built for frequent power cycles!
Thanks a lot!
Obviously, it is not possible to switch the ventilation unit with live potential at the L1 terminal! Possibly, the unit will be damaged if this would happen. The conclusion:
(a) A Shelly for switching the unit on/off is omitted.
(b) Thus, only two Shellies are used - for switching to middle and high position.
This is the appropriate diagram:
Brilliant question!
For a double check, I would have a look at your very first picture in this thread - but without your diagram! Just the sketch out of the manual.
Habe mir doch die 17 Minuten angesehen (man gönnt sich ja sonst nichts). 3 mal Miele-Werbung übersprungen…
Meine Erwartungshaltung wurde erfüllt! Wir haben im Forum übrigens einen Thread mit rd. 300 Posts, in denen das ganze Thema vor- und rückwärts debattiert wird. Da findet man ähnliche Weisheiten, wie im Video…
Das ist der Monster-Thread:
Welcome to the forum!
Would you please draw a little sketch how you’ve wired the Shelly and the switches?
Hope you may follow my thoughts with this sketch:
Aim is, to power L2 and/or L3 only with a running ventilator.
Es wurde bemängelt, daß die Ansicht der Unterseite der Relaisbaugruppe fehlt. Das hole ich gern nach:
Der Sicherheitsabstand zur Erfüllung der SELV-Vorschriften ist ausreichend bemessen!
Die Schaltung der Baugruppe:
Q1: NPN-Transistor mit SMD-Code „64“.
D1: Diode mit SMD-Code „A“
R4: NTC (Raumtemperatur 8,8kΩ)
R5: 10kΩ
If live potential has to be connected to pin L1 to turn the ventilator on, your sketch is fine! But I would recommend to wire the „I“ terminals of the Shelly in the middle and in the right to L1. Don’t know what happens if L2 and/or L3 are powered without powering L1! With my recommendation, you would avoid faulty situations…
Welcome to the forum!
Would you please draw a little sketch how you’ve wired the Shelly and the button?
Your diagram shorts permanently pins L1, L2 and L3. Thus, functionality has gone…
Due to the fact, you want to control 4 possible states: O=off, 1=low, 2=middle, 3=high, you need at least two dry contacts and a central on/off switch. But the Shelly 2.5 doesn’t have dry contacts!
I would recommend
(A) a Shelly pro 2 (two separate dry contacts for the intensity) and a Shelly pro 1 (to switch the ventilation on/off), or
(B) three Shelly 1 (two for the intensity, another to switch on/off).
(A) has the merit to be mountable on a DIN rail - but is more expensive than (B).
Wenn die Betriebsanzeige am Shelly UNI während des Klingelns erlischt, ist das ein Zeichen dafür, daß die Betriebsspannung zusammenbricht! Messen ist angesagt, wie Eulhofer bereits andeutet hat!
Good item in a perspective of efficiency and economy!
If you don't need energy metering for the 3-phase pump, you may switch on/off the (required!) contactor with a simple Shelly 1 or Shelly pro 1 (montable on a DIN rail and with LAN-Socket)). This Shelly switches in parallel also the Aseko unit.
IIRC, your Shelly plant for the pool is equipped with pro-series only (1x Shelly pro 1PM and 1x Shelly pro 1), which are fully equipped with LAN sockets.
Perfect! Hence, the Aseko unit may be supplied (and switched) in parallel to the coil of the contactor.
The Shelly EM is quite good in energy metering, but is (like the Shelly 3EM) suited to switch contactor coils. Due to the fact its relay is capable to switch max. 2 A current (approximately 400 W), the Shelly EM is not able to switch larger applications.
Habe mir zu Studienzwecken den Fibaro-Bypass besorgt: Ein vergossenes Bauteil, das sich jeder Untersuchung widersetzt. Ein elektrischer Check ergab, daß es nicht zur Speisung von Shelly Dimmer2 und 1L ohne N-Leiter geeignet ist!
Eine Alternative zum Shelly Bypass zum Zweck, einen Shelly 1L oder Dimmer2 OHNE Neutralleiter zu betreiben, gibt es nicht! Der Bypass ist speziell auf die beiden genannten Shellies abgestimmt.
Soll der Bypass jedoch dazu dienen, bei Shelly Dimmer2 MIT Neutralleiter ein Flackern bzw. Flimmern zu verhindern, so ist der Bypass ohnehin nicht dazu gebaut. Hier hilft m.E. nur der Tausch des Leuchtmittels (siehe LED-Kompatibilitätsliste im Forum).
Thanks for the detailled info!
To question C: Assuming, the wattage of the Aseko unit is not very high, I would recommend to add the live wire to Aseko unit to the coil wire of the 3-phase contactor. Would you please indicate the wattage of the Aseko part for a double check?
To question D: Unfortunately, an Add-On is not available yet for Shelly pro series. Thus, you would have to invest an a separate Shelly 1 with an Add-On.
SparkyMaster schrieb:
"Meine Vermutung ist, es kann sich nur um das Layout der Platine handeln, siehe SELV-Konformität."
Die SELV-Konformität wird bei dem untersuchten Shelly pro 2 durch Sicherheitsabstände an den beiden Relais erreicht. Da sehe ich keine Einflußgröße.
@AlexAn : Die Versorgung mit 24V DC ist ja immerhin möglich
, auch ohne separate 12V-Klemme…
Mit dem Schaltkontakt des Shelly EM wird ja (planmäßig) nichts geschaltet - das Abschalten einer PV-Anlage ist nicht empfehlenswert. Möchte man den Shelly EM als Gerät schützen, kommt eine zusätzliche Feinsicherung (250mA flink) in Frage. Die wird zwischen der Klemme, an der Spannung abgegriffen wird (in Deinem Fall der 25A LS-Automat) und der Klemme L des Shelly eingefügt.