    I have this from my electrician, looking at the circuit diagram:

    "Its asking for a feed from the main switch and the two circuits we’ve clamped. The concern is the meter tails are huge and the terminal is small so there’s no easy way to do that. And i’m concerned that it will trip the rcbo’s due to line / neutral imbalance."

    Anything I can feedback to him, paerticularly on that last comment?

    Thanks. In investigating myself I can see the terminals A and B arent connected - hence the missing voltage etc reading.

    My configuration is clamp C on the main property (UK, domestic) line in. Then clamps A and B on internal circuits that run from the property consumer unit.

    I have the shelly set to monophase and each of the clamps is set to 120A.

    The electrician is concerned about connecting two additional 240v lines to the shelly. Is there anything else to tell him to be careful of, or is it as simple as making those last two connections, from the consumer unit on the breakers to ports A and B on the Shelly?