How to connect to a 3 phase network without neutral
  • Dear,
    i hope somebody knows...
    In belgium we have some electrical networks that don't supply a Neutral to the home.
    So the network is 3x230V i.s.o 3x400+N ....
    The shelly 3EM requires a N to be supplied ... probably to measure the voltage per phase.
    Is it possible to power the 3EM without neutral ?
    Worst case i need to wire it up as 1 phase... but then the information of voltage per phase will be lost so the wattage will be slightly of.
    Or does the 3EM measure the phase between voltage and current ? if yes... it's unusable.
    thnx...
    Einmal editiert, zuletzt von barry2002 (19. September 2020 um 06:05)
  • SparkyMaster 19. September 2020 um 10:00
    Hat das Label Shelly 3EM hinzugefügt.
  • So i tried ... powering the 3em in a one phase way...
    but then the powerfactor (phase) is not correct.
    So if we would be able to manually adapt/adjust/offset the phase we could get it to work in some way.
    Is there a way to get the voltage & current history ... because this is always correct?
  • I suppose you have 3x220V. Then, I think you can connect N, Va, Vb, and Vc, using a small (25 - 50VA max) 1:1 transformer Delta to Star. In the secondary you will have the same 3 phases that you have in primary plus N.
    Good luck.
  • I think a Delta-Star transformer will not be the solution.
    If I remember correct when using 1:1 transformer in delta-star configuration there will be a phase shift of 30° between primary & secondary.. resulting again in a bad powerfactor at measuring side of 3EM.
  • Dieses Thema enthält 35 weitere Beiträge, die nur für registrierte Benutzer sichtbar sind.