Convert Old Doorbell to Smart, but a little different

  • Hi, I would like to chime in here (pun intended

    Externer Inhalt static.xx.fbcdn.net
    Inhalte von externen Seiten werden ohne Ihre Zustimmung nicht automatisch geladen und angezeigt.

    ).

    I am renewing the making smart of my old dumb doorbell, which works on 8V AC.

    What i did a several years ago, was to add a Finder relay (22.21.8.008.4000 → NO) in series with the doorbell circuit. That finder Relay has dry output contacts, with a 433 sender attached to it.

    Result: when the doorbell was pushed, the 2 existing chimes worked, and as an extra, the Finder relay closed so the sender (433Mhz) sent a signal to an extra wirelsess chime, and the signal was also picked up by my RFXCom.

    I would like to eliminate the RFXCom, and the 433 MHz protocol, by adding a Shelly Uni Plus.

    The Shelly has its power from the 8VAC doorbell trafo, that works good.

    I would now like the dry contacts from the Finder relay as input for the Shelly, to detect the Doorbell push. I used the GND (green, 7th wire) and the IN1 (orange, 9th wire) for that, but that gives me a constant push.

    Has someone an idea how to wire a simple short circuit (like a button press) as input for the shelly uni plus?

    I can also see in HA events happening.

    The issue I have is that the sender device for 433 MHZ is also still connected (attached them in parallel), but that device keeps getting continuous signal, like it 's short circuited fulltime, that’s what makes me think this is not ok.

    I manually shorted Gnd and IN1, that gives me 3 events in HomeAssistant…

  • Wim van Eupen 15. Februar 2025 um 11:04

    Hat den Titel des Themas von „Convert Old Doorbell to Smart, but a liittle different“ zu „Convert Old Doorbell to Smart, but a little different“ geändert.
  • The issue I have is that the sender device for 433 MHZ is also still connected (attached them in parallel), but that device keeps getting continuous signal, like it 's short circuited fulltime, that’s what makes me think this is not ok.

    Hello Wim,
    if you want to use also the 433 Mhz sender, you should connect it to the output from the shelly uni, instead of the relay contact. The contact should have only one connection, to the shelly.
    Relay triggers uni, uni triggers 433 Mhz sender...
    You could also replace the relay, type 22.22.8.008.4000, this one has 2 dry contacts...

  • horkatz thank you so much. This was a step I was about to be testing, but your comment made me do it right away.

    This works. I configured the input as button, the output type as activation (with auto power off after 1s).

    Now i need to figure out how to use the events to automate my doorbell, but that should be possible ...